I am trying to wire up my shop with the thought of getting a 1 phase 2.2 HSD spindle and was wondering what size wire and breaker to get. The run form the panel is 50 feet.
bob_s
08-09-2009, 12:53 PM
you will need a 30 amp 220 breaker if it is a HSD 2.2 horsepower spindle from Shopbot.
#10 should do it even with a 50 foot run, but I would check with your local code authority to be sure. I think if it is type THHN wire in conduit you can use #12, but I wouldn't do it for the tiny cost savings.
jim_vv
08-09-2009, 01:10 PM
I have the 2.2 single phase spindle and we wired exactly how Bob recommends. The nameplate on the VFD reads 230V / 17.5A.
#10 is rated at 30amp so it works with no problem. Just make sure you have a good ground setup as I've found the PRS Alpha to be a little sensitive if your ground system is not good. Also, make sure you have a really good grounding system for the entire Shopbot all tied into the electrical ground. We used the grounding recommendations outlined, I think it was, in the Shopbot Wiki.
Don
www.diamondlakewoodworks.com (http://www.diamondlakewoodworks.com)
ricky_spearman
08-09-2009, 11:34 PM
I had to drive a seperit, 14ft. ground stake and used #6 copper straned to the Electrical box and to the control box to eliminate stay signals and noise.
It's not fun when you have to track problems down.