Do any of you have heated floors in your shops? Are they electric or solar hot water? If electric what is the operating cost? :confused:

dlcw
01-18-2014, 07:54 PM
My 40' x 80' shop is radiant floor heating. Wouldn't trade it for anything. I have 16' ceilings at the peak and I couldn't justify sending a bunch of heat that high up since my head will never get up there (other then to change light bulbs once in a while.

I put all the tubing in myself over 3" pink panels. The concert is 4" thick with fiberglass reinforcement in it to make it unnecessary to have rebar.

I keep my floor thermostat set at about 72 degrees and I am VERY comfortable even when we are having a temperature streak in the negative numbers to single digits for for highs 10 days to 2 weeks.

Since out electric is $.038 per kilowatt hour, I went with a 100amp on demand boiler. The other option was propane but when we ran the numbers electric was about half the cost of propane.

We have a 800 sq ft appt in the shop so we use a water heater, electric drying, electric oven/stove, plus other appliances and when I combine that with all the power tools, central dust collection, CNC, etc. with the radiant floor system, my monthly electric bill is around $245/mth. When I shut the radiant system off in the summer my bill drops to about $85/mth. Not bad considering I'm heating a 3200 sq ft building with 16' peaked ceilings.

gene
01-18-2014, 08:45 PM
Don
What type of ceilings and insulation do you have?

myxpykalix
01-18-2014, 10:20 PM
Don,
What i don't understand is how, if your shop air is cold, tools, and other things how does heating your floor make other things warm? Or when you walk in your feet might be warm but when you touch stuff it's all cold?

I understand that heat rises and you have a on demand system so i assume you turn the heat off to the shop when not in use right? If so how long does it take to get the shop warm enough to work in?:confused:

scottp55
01-19-2014, 09:14 AM
Jack, entire house is hydronic radiant(2800 ft tubing) run off indirect propane boiler.Wouldn't trade for anything. Water going to tubing is controlled by external temperature probe and an algorithm to control the mixing valve for the water temp going to the tubing. Water going to tube NEVER goes above 80F. So floor never feels warm to bare feet. 6" slab/tubing stapled to 2" blue foam(so it's at the bottom-away from the coring/expansion cut every 12'). It is not a fast on/off type heat. When I started working in shop(12x24x8') I just cracked the shop valve(200' tubing) and shop never goes below 50F even in the 0F we just had. But I do open the adjoining fire door to the house when I'm working and within an hour it's 65F. With valve closed the thermal mass of the concrete alone it Never got below 45F ever in 18 years. 12"insul in 2x12 rafters, 6" in walls in shop.
Jack, it's radiant(think a giant 85F woodstove). It heats ALL the objects in the room in a straight line from the floor. THEY warm up which heats the room air. Lost power 3 days in sub zeroF 5 yrs ago and in those 3 days house only went down 10 degrees. It takes a long time for the heat to come up-BUT it takes a long time for the heat to go down also. The heat you put in today, will mostly still be there tomorrow. Put thermal breaks in so slab doesn't touch foundation.
You can also set it up to run COLD water(AC) but you want to make sure you run either a de-humidifier OR keep the water above the condensation temp or you'll have "Dew" on your floor and mold problems.

gpinard
01-19-2014, 01:49 PM
Hi, I also have radiant heat. About 4500 sq ft on 3 floors. Basement workshop 4” concrete on 2” insulation, tubing attached to 6x6 wire mesh at mid slab, 2 upper floors of living space 1 ˝” concrete topping slab on wood structure. The thermal mass on the living floors is less at 1 ˝” thick so it reacts a little quicker than Scott describes, but still takes a couple of days to heat up or cool off. Mine is an heating oil fired boiler, not as economical as when I made the decision to use oil in 2001, but still reasonable for the sq ft. To do it again I might change the source but not radiant, it is wonderful. The best way I have found to describe it, is heat is a non-issue, you come in the space and are comfortable.
Radiant heat is a little different animal to understand, I can add to Scott’s description a little. On a cloudy day when the sun pops out and shines on you, you feel the warmth, and yet the air temp has not changed. The sun is radiating energy to you. In the grocery store in front of the freezer case, if you measured the air temperature you might find it to be a couple of degrees less than in other areas of the store, not enough to explain the cold you feel in front of the case. You have become the radiator and are providing heat to the colder object. When the mass of your building and the objects in it are at a compatible temp with your body, you are comfortable. One common misconception is that heat rises. This is not true. Heated AIR rises. In a forced air system, over temp air is pumped into the space warming you and objects as it races UP, displacing air that has cooled from the ceiling. This creates a lot of air circulation and movement. Radiant heat does heat the air but only up to the temp of the surrounding objects, there is a lot less air movement in radiant, the ceiling and roof are cooler. In my home we have a big window wall, this is an area of greater heat loss. In the winter as you approach the windows, you would become the radiator, so the radiant panel (the area of tubing in the concrete topping slab) is run at higher temp, the panel in front of the windows delivers more energy to counter act the area of greater heat loss, so it remains a neutral environment for the occupant. Think the check out at Home Depot, with the roll up door open in the winter, look up and see the gas fired long 4” tube glowing orange above the checkouts. A radiant source delivering energy directly to you in spite of the greater heat loss.
Dan Holohan is the author of an excellent book on the subject, “Hydronic Radiant Heating, A practical guide for the non-engineer installer”

steve_g
01-19-2014, 02:51 PM
Jack…
Just to add to the caveat expressed by others…
I remember with great fondness laying on our radiant heated floor and playing with my trains… My parents hated it as the house was always catching up to the cold, or grossly over heated as millions of BTU’s of stored energy in the slab dissipated. When I built their new house, we used perimeter hydronic radiators that they were very happy with.

SG

gpinard
01-19-2014, 05:46 PM
We also experienced what Steve described. In days that the outside temperature had a larger swing, the system could not react quickly enough to the falling outside temp, so the house temp would cool off. The system is calling for and delivering heat. Then as the outside temp rises and the house has been calling for heat, it ends up overshooting the mark. For us it was not a big deal, we noticed it, but it was not uncomfortable. On days with not so large of temperature swing we did not even notice it. Whether it is cold or warmer is not the issue, only the change in outside temp thru the day.
About 4 years ago I upgraded the controls for the boiler to a computer based (Scott’s algorithm) control. The new control eliminated the problem and paid for itself in fuel savings that year. I think now the simplest computerized controls take care of this problem.

dlcw
01-19-2014, 06:59 PM
Don
What type of ceilings and insulation do you have?

My shop building is constructed using structured insulated panels (SIPS). The eve walls are R-30 and the gable end walls are R-36. The ceiling has 30" of insulation giving it an estimated R value of around 64+. The SIPS make the building virtually air tight.

I have to keep windows open a crack to keep air circulation. Some day I might add a air handler to move the air around but the down side would be introducing moving air around (moving dust everywhere).

dlcw
01-19-2014, 07:06 PM
Don,
What i don't understand is how, if your shop air is cold, tools, and other things how does heating your floor make other things warm? Or when you walk in your feet might be warm but when you touch stuff it's all cold?

I understand that heat rises and you have a on demand system so i assume you turn the heat off to the shop when not in use right? If so how long does it take to get the shop warm enough to work in?:confused:

The shop air up to head level is warm thus making all the machines warm (reduce or eliminate rust potential). Anything above head level does not need to be heated.

The heat stays on all winter. It takes a lot more energy to heat things up then to keep things at a constant heat level. Since I also have my "apartment" in the shop building, I keep the thermometer set and don't vary it. When it starts to warm up in the spring, I back the thermostat down a few degrees. It takes more then 24 hours for the slab to change 1 degree up or down in temperature. Remember, I'm not heating air. I'm heating a massive concrete slab which radiates the heat from it. We can have 5 to 7 day power outages and the temp in the shop building stays comfortable even in the coldest temperatures.

At some point I will think about a backup electrical generator in the case of longer black outs like what happened in 1997 when there were places without power for 6 to 8 weeks in the dead of winter after a huge ice storm took the power distribution grid apart.

coryatjohn
01-19-2014, 08:57 PM
>> what happened in 1997 when there were places without power for 6 to 8 weeks in the dead of winter

I can't imagine what that would be like. The longest I've ever suffered a power outage for was about ten hours. That's in 56 years of life.

t28c34
01-19-2014, 10:11 PM
Thats what has worried me since i put my heated floor in. I picked up a good deal on a 7000 watt generator this fall, so im covered. My shop is 1800sf pole barn with 12 foot walls and open rafter area. bought the palce 3 years ago and had to pour the floor in. The walls are insulated but not that great as far as i can tell. Ceiling rafters are enclosed but no insulation. The entire inside of the shop is caulked and sealed with 1/2 inch chip board. The floor water is heated with a propane on demand water heater. We strugled though the first winter with a HUGE propane bill and could not get the shop near 60 degrees on really cold and windy days unless the heater ran all day. The floor and sides of the slab have 4 in foam so i know its not the problem. I think it is just a poorly insulated building.
Janruary of 2013 is when we stoped using propane for heat in the shop and our 1900sf house. We now heat useing a Central Boiler 2400 outdoor wood boiler for heating the shop floor and house. I can keep the shop at 68-70 degrees on cold windy days, and the house at 72. But with that polar vortex thing that passed though i had trouble. I had to break down and give the major heat load to the house. Just to darn cold, the wind was going right though the shop. had to turn it down to 40 degrees, where it was stable.
Now for how much wood i use? Well my brother runs a sawmill so wood is not hard to find. Just a matter of keeping ahead with seasoned wood. 2013/2014 is my first full heating season and i have gone through about 10 cord of wood. The boiler works best with seasond wood, which i have yet to keep ahead of.

myxpykalix
01-20-2014, 02:23 AM
has anyone installed electric heating in their floors?

gpinard
01-20-2014, 08:33 AM
Jack
I put an electric snow melt system in a 40x60 approach apron to a fire station. rebar grid to support what looked like 12 ga romex wiring. 200 amp service to run it. no idea about costs to run it.

mwpfeifer
01-20-2014, 09:27 AM
I also have hydronic in-floor/baseboard heating in my shop and home. I can't really provide any really accurate numbers as to cost to heat but I use between 10 to 12 cords of firewood in my Central Boiler outdoor furnace. Firewood is readily available here in northern MN at a cost of about $80 dollars a cord delivered in log length ( I get some much needed summertime exercise cutting and splitting this into shorter chunks). The house (1800 sq ft)stays at a constant temp of about 68-70 degrees with the circulation pumps turning off and on as the thermostat demands. Biggest problem I have is regulating the temp in the shop as it's a poorly insulated 24x30 pole barn that I have converted into my shop. If I can keep the temp at about 60 degrees I can usually keep the snow on the roof from melting and creating ice dams otherwise I get a few minor leaks. Still working on finding and getting those fixed each summer. This system has a propane backup in the event we have to leave for a few days and there is a small generator that handles the circulator pumps in the event of a power failure.

dlcw
01-20-2014, 12:32 PM
>> what happened in 1997 when there were places without power for 6 to 8 weeks in the dead of winter

I can't imagine what that would be like. The longest I've ever suffered a power outage for was about ten hours. That's in 56 years of life.

There was a huge ice storm that took out virtually the entire above ground power grid. This is a VERY rural area and people back in the sticks were the ones without power for so long.

chunkstyle
01-20-2014, 02:25 PM
Jack,

We put in radiant floor heating in the 1st and 2nd floors of the shop/studio. We also went with a condensing boiler using propane. Since were out in the fringe a bit and ice storms have been known to occur I hung a non-venting convection wall heater in the downstairs area in case I need to throw heat into the shop while the power is out.

We went with a Munchkin boiler that was also being branded for Peerless.
Biggest problem we had was the control panel design. I attribute that to over reliance on the design software the HVAC company used to calculate the heads of the diferent circuits and size pumps accordingly. Real world conditions proved them wrong and the zones never functioned as they were designed to. Lots of short cyling of the bioler and fault outs.Talking to many installers on job sites has given me a better understanding of what really works in the field and why. I plan on tearing into control panel this spring and redoing the zone pumps and boiler loop. Just a word of caution there. It is a balancing act of components. I had my panel done by a large company that did nothing but this style of heating.
Also, I don't feel a high efficiency condensing boiler is what I would do again knowing what I know now. Parts are very expensive and the first time you need to replace something you've just blown any perceived savings in fuel costs. I would look at a high output hot water heater for reliability and maintenance costs. As it is I am looking at a $400.00 fan bill right now as the circuit board leaks a little voltage to the fan causing it to turn a very slooow rpm but its enough to fault out the boiler. Nope, that pc board is not available by itself. Gotta buy the whole fan unit. Sigh... Simpler is better when it comes to sub zero nights in the middle of January IMHO.
The heat is great though and I couldn't imagine heating a shop any other way.
As always, my insight is worth what you paid for it.

Tim