harryball
02-10-2015, 12:57 PM
I did a few searches and reading on previous topics.... I THINK I know what to do both short term and long term but I thought I'd ask.
My new shop has twin 200A panels. The Neutral-Ground bond is made in the meter box not in the panels. As such, the panels have split Neutral / Ground bars. (done by licensed electrician and inspected)
However, my subpanel I uninstalled and transported from my previous shop sports ONLY a ground/neutral bar and the previous shop had a Neutral-Ground bus that was bonded as one. (licensed electricians did all this and it passed inspection). In addition my bot chassis itself was grounded directly to its own ground rod. It always worked, never had comm problems.
Now I'm in the new shop and I'm not sure how to approach this.
The subpanel feed has two hots and a ground for 220V.
Option 1)
Leave it as is (was) with the neutrals from the bot (there are only two 110V breakers) bonded to ground and leave the ground bonded to the main panel. Add a direct chassis ground to drain off static and any leak currents.
Option 2)
Same as above, but do NOT use the ground wire in the feed but rather ADD a ground wire from the ground bar in the subpanel direct to the SAME grounds as the main panels. This should prevent any potential neutral feeds from leaking through the main panel grounds.
Option 3)
Replace it all with a new subpanel and 3/C+G wire. Then add a chassis ground. My least favorite option.
I'm not worried about comm problems, if I have those I'll do what's needed when I encounter them up to and including option 3. I'm more concerned about SAFE. So long as Option 1 (or 2) is SAFE and I don't have comm errors I'm fine.
Non-binding and non-accountable opinions?
/RB
My new shop has twin 200A panels. The Neutral-Ground bond is made in the meter box not in the panels. As such, the panels have split Neutral / Ground bars. (done by licensed electrician and inspected)
However, my subpanel I uninstalled and transported from my previous shop sports ONLY a ground/neutral bar and the previous shop had a Neutral-Ground bus that was bonded as one. (licensed electricians did all this and it passed inspection). In addition my bot chassis itself was grounded directly to its own ground rod. It always worked, never had comm problems.
Now I'm in the new shop and I'm not sure how to approach this.
The subpanel feed has two hots and a ground for 220V.
Option 1)
Leave it as is (was) with the neutrals from the bot (there are only two 110V breakers) bonded to ground and leave the ground bonded to the main panel. Add a direct chassis ground to drain off static and any leak currents.
Option 2)
Same as above, but do NOT use the ground wire in the feed but rather ADD a ground wire from the ground bar in the subpanel direct to the SAME grounds as the main panels. This should prevent any potential neutral feeds from leaking through the main panel grounds.
Option 3)
Replace it all with a new subpanel and 3/C+G wire. Then add a chassis ground. My least favorite option.
I'm not worried about comm problems, if I have those I'll do what's needed when I encounter them up to and including option 3. I'm more concerned about SAFE. So long as Option 1 (or 2) is SAFE and I don't have comm errors I'm fine.
Non-binding and non-accountable opinions?
/RB