Hi guys -
I am curious as to how many 120V circuits you are using for your router. Could you kindly post what you have plugged into what circuit?
For example....
Circuit 1
- Computer
- Monitor
- Controller
Circuit 2
- Routers
Circuit 3
- Dust collector
I am trying to figure out what is really the best set up and I thought that I would ask the guys that know....
Thanks in Advance for your help.....
Mark
Gary Campbell
08-31-2008, 05:46 PM
Mark..
Dont know if this all applies to you, but with our PRSa & spindle:
Circ 1:
30A 240V Spindle
Circ 2:
30A 120V Control Box
Circ 3:
20A 240V Dust Collector
Circ 4:
20A 240V 4 head Vac hold down
Circ 5:
20A 120V isolated ground Computer UPS with comp & monitor on it.
Hope this helps
Gary
bsilva
08-31-2008, 09:01 PM
I have a PRS standard with a 2.2HP spindle:
1) 240V 25A: Spindle
2) 120V 15A: SB
3) 120V 20A: Dust Coll (Harbor Freight 2HP with a real filter)
4) 120V 15A: Vac & Utility
5) 120V 15A: Design Computer, Stereo, other important things. ;-)
Works Great!
Brad
jamesgilliam
08-31-2008, 11:25 PM
1. 120V 20A Router
2. 120V 20A Computer, SB control box
Not using dust collection at this time, easier to get the leaf blower and send it out the back door.
maginter
09-01-2008, 09:00 AM
Thanks for the input...
It sounds like there are no real Do's and Don'ts except have some decent power supplied.
Thanks
dana_swift
09-01-2008, 10:49 AM
Mark-
My setup also includes a circuit for an air-compressor. The compressed air drives a pneumatic wrench. All my fixtures are bolted to the table, and I change fixtures very very often and the compressor runs frequently while the router does.
Sometimes I also use the compressed air to blow away chips when the dust skirt is not in use.
And also I run clamp on lights around the router so these old eyes can see what is happening better.
In my case add two 20A 110v circuits to all the ones already listed in the previous posts.
D
chiloquinruss
09-01-2008, 11:56 AM
Woodshop Stuff
1) 240V 30A: 4hp Spindle
2) 120V 30A: ShopBot Standard
3) 240V 30A: Dust Collector
4) 240V 30A: Cabinet Saw
5) 240v 30A: 19in Band Saw
6) 240V 30A: Compressor
7) 120V 15A: Computer (isolated)
8) 120V 15A: Stuff!
Design Center is all 120V 15A stuff.
Good Thread, thanks for starting it! Russ
maginter
09-02-2008, 02:19 PM
How are you guys, "isolating" your computer, electrically?
Gary Campbell
09-02-2008, 05:44 PM
Mark..
Electrician installed a dedicated circuit with isolated ground. Then we use a UPS for surge & a few minutes for shutdown.
Gary
wberminio
09-02-2008, 06:12 PM
We installed a dedicated sub panel to the Shopbot location.The control box,spindle,vacuum,and computer
all on separate circuits.
Erminio